Mark from Pennyslvania asked:

Hi, the previous Pro on my roof did not use long enough nails on my vent ridge and the wind blew it back or peeled it up, the shingle still intact. Would it be Ok if I just took longer nails and put them every foot or so on both sides then put a good caulk over the heads instead of peeling it all back off and doing it with the proper nails? Thank you.

April 4, 2023 at 12:03 p.m.

alextolle
Below is what our roofing expert John Kenney from Cotney Consulting Group had to say in response to your question:
 
Hi Mark,
 
I will assume that the type of vent you describe is a 10ft Aluminum Ridge vent installed on a shingle roof.
 
The correct method to install a ridge vent over one shingle roof system is to use a 12 gauge, 1 ¼” aluminum or galvanized corrosion-resistant ring shank nails every 6” on-center along both flanges. The fasteners should not be placed within 2” from the end of the ridge vent sections. Seal the exposed nail heads. Use caution not to block any drain holes with sealant.
 
If there is no damage to the shingles or vent, it could be refastened correctly. If the existing nails are 1-1/4” and not holding, you should use longer nails that penetrate through the decking by ¾.”
April 4, 2023 at 12:04 p.m.

alextolle

Mark followed up with:

It is the plastic vent ridge then the shingles on top it leaves a space about 1/2 an in from the roof surface. I wanted to see if I could just put the longer nails in the existing shingles on the Ridge Vent and put a good caulking over the nail heads instead of removing and reinstalling a new Ridge Vent and New shingles with the correct nail lengths this time. I realized the part that got blown back off had only 1/8" to 3/16" sticking in the sheeting and did the repair on that with new shingles. Thank you for your valuable input, it is greatly appreciated.

April 4, 2023 at 12:04 p.m.

alextolle

John Kenney from Cotney Consulting Group said:

 

Mark,
 
I appreciate you clarifying the type of ridge vent you have. I would not recommend just installing longer nails and using chalk on exposed nail heads.  
 
Though that fix sounds like a good solution, and you need the proper length nails to penetrate the decking by 3/4" to prevent the same issue from happening again. Expansion and contraction from varying temperatures will cause the nails to move and break the caulking seal leading to leaks.
 
The only proper fix is installing new ridge cap shingles per the manufacturer's recommendations with the correct length specified nail.
May 24, 2023 at 11:05 a.m.

laurenwhite
John at Go Roof Tune Up said:

From your description of the problem, it appears that proper fasteners are a good solution for the problem. Choose a nail that is of proper length to set into the wood sheathing by at least ½”. Install sealant on the surface of the shingle. Drive the nail through the sealant for a proper seal. Be careful to not overuse sealant. Mastic or other sealants may have an adverse effect on the surface of the shingles. Hope this information helps.

 
Your Friends at Ask A Roofer.

« Back To AskARoofer
You must be logged in to reply to this topic.

Social Feed


Follow Us
Westlake - Sidebar Ad - Special roofing that rises above it all
Tremco - Sidebar Ad - Restoration Guide
IKO - Sidebar - Summit Grey
WTI - Sidebar Ad (AAR) - Pure Air February 2024
AAR - MRA - Sidebar Ad - Buyer
Western Colloid - Sidebar Ad - Understanding Commercial Roof Restoration (eBook)